hi everyone
We have fin tube type cooler that is used to cool MDEA upto required tempeartures. But we are having some problems in gaining required temperatures..it looks that inside tubes have been corroded or scaled because at 100 % fan speed and with all the louvers open we are not gaining the desired temperatures..can anyone tell me what could be the possible reason...or what else i can do to gain the desired temperatures...or any other method???
Thanks
|

Fin Tube Cooler Temperature Variations
Started by burrows85, Sep 07 2011 02:29 AM
5 replies to this topic
Share this topic:
#1
Posted 07 September 2011 - 02:29 AM
#2
Posted 07 September 2011 - 03:57 AM
If there is not visible scale outside and fan operates properly, there must be scale inside the tubes (fouling), which needs cleaning. You can try chemical cleaning before dismantling for mechanical cleaning (pigging is not assumed to be applicable). (http://www.cheresour...h__1#entry50380 gives few info on scale cleaning)
#3
Posted 07 September 2011 - 08:13 AM
Also check fan belts for slippage and measure actual power consumption/amperage of the fan motors. In addition to that, check behavior of the controllers acting on the motor and those controlling actual position of fan louvres. It could be a simple issue.
Once when you verify these parameters and find them OK you can start thinking of cleaning the tubes.
Once when you verify these parameters and find them OK you can start thinking of cleaning the tubes.
#4
Posted 12 September 2012 - 12:58 AM
Dear ,
Recently i have been attributed , responsibility for cleaning of fins of heat exchanger of air cooler. I have recieved quatations from vendors also.
like chemical cleaning with biodegradeble surfactant, high pressure water cooling, high pressure steam cleaning ( 8 barg )
What are the things i should check so that the cleaning shall be done with out no harm to exchanger or environment
Recently i have been attributed , responsibility for cleaning of fins of heat exchanger of air cooler. I have recieved quatations from vendors also.
like chemical cleaning with biodegradeble surfactant, high pressure water cooling, high pressure steam cleaning ( 8 barg )
What are the things i should check so that the cleaning shall be done with out no harm to exchanger or environment
#5
Posted 12 September 2012 - 07:25 PM
Shin,
What about cleaning the outside of the fin where dirt is accumulated ? How do you consider it?
Breizh
What about cleaning the outside of the fin where dirt is accumulated ? How do you consider it?
Breizh
#6
Posted 13 September 2012 - 07:27 AM
Personal knowledge is limited to finned tubes of fuel oil boiler economisers, cleaned (without apparent problems) through high pressure (~20 barg) steam sootblowers. Yet this cleaning occurs e.g. twice per day, not once through. And scale from flue gases may differ to that from ambient air. One could get an idea of the methods by googling e.g. "fined tube cleaning", for instance http://www.tubetech.com/case-studies/process-manufacturing/fin-fan-cleaning-improves-heat-transfer/.
Combination of a surfactant with HP steam or water (once at a time) could be a more drastic way out; however I would confirm free disposal of resulting wastewater for the specific case, even if the surfactant is biodegradable http://en.wikipedia....wiki/Surfactant .
Specific experience from air coolers cleaning could give a more concrete answer. For want of something better, web could give a picture, e.g. http://www.hudsonpro...nfan/FfFaq.html - etc*, http://books.google....leaning&f=false, http://www.sentro-tech.com/category/ff '> http://www.sentro-tech.com/category/ff .
* question on cleaning refers to "cleaning page" of websire, not found.
Combination of a surfactant with HP steam or water (once at a time) could be a more drastic way out; however I would confirm free disposal of resulting wastewater for the specific case, even if the surfactant is biodegradable http://en.wikipedia....wiki/Surfactant .
Specific experience from air coolers cleaning could give a more concrete answer. For want of something better, web could give a picture, e.g. http://www.hudsonpro...nfan/FfFaq.html - etc*, http://books.google....leaning&f=false, http://www.sentro-tech.com/category/ff '> http://www.sentro-tech.com/category/ff .
* question on cleaning refers to "cleaning page" of websire, not found.
Edited by kkala, 13 September 2012 - 08:03 AM.
Similar Topics
![]() Pipe Fluid Temperature Increase Due To Solar LoadingStarted by Guest_HeemeshJ126_* , 06 Apr 2016 |
|
![]()
|
||
![]() Distillation Tower Top And Bottom Temperature And PressureStarted by Guest_student55_* , 27 Mar 2016 |
|
![]()
|
||
![]() High Stack Temperature In Ccr HeatersStarted by Guest_viba0124_* , 30 Nov 2024 |
|
![]() |
||
![]() Rotated Triangular Tube Layout Vs Triangular Tube LayoutStarted by Guest_Heat Transfer Novice_* , 28 Sep 2024 |
|
![]() |
||
![]() Supercritical Fluid Flowrate - He Tube RuptureStarted by Guest_flarewolf_* , 07 Apr 2025 |
|
![]() |